G-code
Revision as of 09:14, 19 January 2015 by Droftarts (talk | contribs) (Introduction)
This page tries to describe the flavour of G-codes that the RepRap firmwares use and how they work. The main target is additive fabrication using FFF/FDM processes. Codes for print head movements follow the NIST RS274NGC G-code standard, so RepRap firmwares are quite usable for CNC milling and similar applications, too.
There are a few different ways to prepare GCode for a printer. One is to use a slicer like Slic3r, Skeinforge or Cura. These programs take a CAD model, slice it into layers, and output the GCode required for each layer. Slicers are the easiest way to go from a 3D model to a printed part, but the user sacrifices some flexibility when using them. Another option for GCode generation is to use a lower level library like mecode. Libraries like mecode give you precise control over the tool path, and thus are useful if you have a complex print that is not suitable for naive slicing. The final option is to just write the GCode yourself. This may be the best choice if you just need to run a few test lines while calibrating your printer.
As many different firmwares exist and their developers tend to implement new features without discussing strategies or looking what others did before them, a lot of different sub-flavours for the 3D-Printer specific codes developed over the years.
Introduction
N3 T0*57
N4 G92 E0*67
N5 G28*22
N6 G1 F1500.0*82
N7 G1 X2.0 Y2.0 F3000.0*85
N8 G1 X3.0 Y3.0*33
Support FiveD Teacup Sprinter Marlin Repetier Smoothie RepRapFirmware
yes automatic no  ??? experimental depreciated  ???
Here means:
yes
The Gcode is fully supported by the firmware.
experimental
There is some support for the Gcode. Often it is required to check out the source code branch for the firmware (usually stored in a different branch) or to flip configuration switches on the mainboard.
automatic
The firmware handles this Gcode automatically, so there's no need to send the command. An example is power supply on/off Gcode (M80/M81) in the Teacup firmware.
It is unknown if the firmware supports this Gcode. You may want to test this yourself before using it in production.
no
The firmware does not support this Gcode.
depreciated
The firmware depreciated this Gcode. The firmware author(s) should amend the depreciated Gcode on this page with workarounds (if needed) and the last supported firmware version that will accept this Gcode.
RepRap G Code Fields
This section explains the letter-preceded fields. The numbers in the fields are represented by nnn. Numbers can be integers (128) or fractional (12.42) numbers, depending on context. For example, an X coordinate can take integers (X175) or fractionals (X17.62), but selecting extruder number 2.76 would make no sense.
Letter Meaning
Tnnn Select tool nnn. In RepRap, tools are extruders
Snnn Command parameter, such as the voltage to send to a motor
Pnnn Command parameter, such as a time in milliseconds
Innn Parameter - not currently used
Jnnn Parameter - not currently used
Ennn Length of extrudate in mm. This is exactly like X, Y and Z, but for the length of filament to extrude. It is common for newer stepper based systems to interpret ... Better: Skeinforge 40 and up interprets this as the absolute length of input filament to consume, rather than the length of the extruded output.
Comments
Gcode comments begin at a semicolon, and end at the end of the line:
N3 T0*57 ; This is a comment
N4 G92 E0*67
; So is this
N5 G28*22
Individual commands
Checking
N and *
These are the line number and the checksum. The RepRap firmware checks the checksum against a locally-computed value and, if they differ, requests a repeat transmission of the line of the given number.
int cs = 0;
   cs = cs ^ cmd[i];
Buffered G Commands
The RepRap firmware stores these commands in a ring buffer internally for execution. This means that there is no (appreciable) delay while a command is acknowledged and the next transmitted. In turn, this means that sequences of line segments can be plotted without a dwell between one and the next. As soon as one of these buffered commands is received it is acknowledged and stored locally. If the local buffer is full, then the acknowledgment is delayed until space for storage in the buffer is available. This is how flow control is achieved.
G0 & G1: Move
yes yes yes yes yes yes
Usage
Variables
Not all variables need to be used, but at least one has to be used
Snnn Flag to check if an endstop was hit (S1 to check, S0 to ignore, S2 see note, default is S0)1
Examples
G0 X12 (move to 12mm on the X axis)
G0 F1500 (Set the feedrate to 1500mm/minute)
G1 X90.6 Y13.8 E22.4 (Move to 90.6mm on the X axis and 13.8mm on the Y axis while extruding 22.4mm of material)
1. G1 F1500
2. G1 X50 Y25.3 E22.4
In the above example, we set the feedrate to 1500mm/minute on line 1, then move to 50mm on the X axis and 25.3mm on the Y axis while extruding 22.4mm of filament between the two points.
1. G1 F1500
2. G1 X50 Y25.3 E22.4 F3000
However, in the above example, we set a feedrate of 1500 mm/minute on line 1, then do the move described above accelerating to a feedrate of 3000 mm/minute as it does so. The extrusion will accelerate along with the X and Y movement, so everything stays synchronized.
The RepRap spec treats the feedrate as simply another variable (like X, Y, Z, and E) to be linearly interpolated. This gives complete control over the acceleration and deceleration of the printer head in such a way that ensures that everything moves smoothly together, and the right volume of material is extruded at all points.3
Notes
1Some firmwares allow for the RepRap to enable or disable the "sensing" of endstops during a move. Please check with whatever firmware you are using to see if they support the S variable in this way, as damage may occur if you assume incorrectly. In Duet-dc42 firmware, using the S1 or S2 parameter on a delta printer causes the XYZ parameters to refer to the individual tower motor positions instead of the head position, and to enable endstop detection as well if the parameter is S1.
Some older machines, CNC or otherwise, used to move faster if they did not move in a straight line. This is also true for some non-karthesian printers, like delta or polar printers, which move easier and faster in a curve.
G2 & G3: Controlled Arc Move
no no no yes1 yes yes
Usage
G2 Xnnn Ynnn Innn Jnnn Ennn (Clockwise Arc)
G3 Xnnn Ynnn Innn Jnnn Ennn (Counter-Clockwise Arc)
Variables
Examples
G2 X90.6 Y13.8 I5 J10 E22.4 (Move in a Clockwise arc from the current point to point (X=90.6,Y=13.8), with a center point at (X=current_X+5, Y=current_Y+10), extruding 22.4mm of material between starting and stopping)
G3 X90.6 Y13.8 I5 J10 E22.4 (Move in a Counter-Clockwise arc from the current point to point (X=90.6,Y=13.8), with a center point at (X=current_X+5, Y=current_Y+10), extruding 22.4mm of material between starting and stopping)
Notes
1The Marlin Firmware can toggle support for these Gcodes. To enable support, make sure to define SCARA at compile time, or else the Gcodes will be ignored.
G28: Move to Origin (Home)
Usage
G28
Variables
This Gcode can be used without any additional variables supplied
Examples
G28 (Go to origin on all axes)
G28 X Z (Go to origin only on the X and Z axis)
When the RepRap firmware receives this command, it moves all (or the supplied) axis's back to the zero endstops as quickly as it can, then backs off by a millimeter and slowly moves back to the zero endstop activation points to increase position accuracy. This process is also known as "Homing".
If you add coordinates, these coordinates are ignored. For example, G28 Z0.00 results in the same behaviour as G28 Z.
When Duet-dc42 firmware is used to control a delta printer, any G28 command will home all three towers, regardless of any XYZ letters.
G29-G32: Bed probing
yes yes yes
G29 Detailed Z-Probe
probes the bed at 3 points.
G30 Single Z Probe
Some implementations allow more general behaviour: if a Pn field is specified the probed X, Y, and Z values are saved as point n on the bed for calculating the offset plane. Generally n is 0, 1, or 2. If X, or Y, or Z values are specified (e.g. G30 P1 X20 Y50 Z0.3) then those values are used instead of the machine's current coordinates. A silly Z value (less than -9999.0) causes the machine to probe at the current point to get Z, rather than using the given value. If an S field is specfied (e.g. G30 P1 Z0.3 S) the bed plane is computed for compensation and stored. The combination of these options allows for the machine to be moved to points using G1 commands, and then probe the bed, or for the user to position the nozzle interactively and use those coordinates. The user can also record those values and place them in a setup GCode file for automatic execution.
G31 Report Current Probe status
In Duet-dc42 firmware, separate G31 parameters may be defined for probe types 0, 1/2, and 3 (probe types 1 and 2 share the same set of parameters). To specify which probe you are setting parameters for, send a M558 command to select the probe type before the G31 command.
Duet-dc42 firmware supports additional parameters S (bed temperature in degC at which the specified Z parameter is correct, default is current bed temperature), and C (temperature coefficient of Z parameter in mm/degC, default zero). This is useful for ultrasonic and other probes that are affected by temperature.
G32 Probe Z and calculate Z plane
probes the bed at 3 or 4 pre-defined points (see M557) and updates transformation matrix for bed leveling compensation.
Unbuffered G commands
The following commands are not buffered. When one is received it is stored, but it is not acknowledged to the host until the buffer is exhausted and then the command has been executed. Thus the host will pause at one of these commands until it has been done. Short pauses between these commands and any that might follow them do not affect the performance of the machine.
Teacup Firmware buffers G20, G21, G90 and G91.
G4: Dwell
yes yes yes
Example: G4 P200
On Marlin and Smoothie, the "S" parameter will wait for seconds, while the "P" parameter will wait for milliseconds. "G4 S2" and "G4 P2000" are equivalent.
G10: Tool Offset
Support RepRapPro Teacup Sprinter Marlin Repetier Smoothie
yes no no (Retract?)  ??? Retract
Example: G10 P3 X17.8 Y-19.3 Z0.0 R140 S205
This sets the offset for tool (or in older implementations extrude head) 3 (from the P3) to the X and Y values specified. You can put a non-zero Z value in as well, but this is usually a bad idea unless the tools are loaded and unloaded by some sort of tool changer. When all the tools are in the machine at once they should all be set to the same Z height.
Remember that any parameter that you don't specify will automatically be set to the last value for that parameter. That usually means that you want explicitly to set Z0.0.
The NIST G-code standard mentions an additional L parameter, which is ignored.
This command is subject to discussion.
Note that Marlin and Smoothie use G10/G11 for executing a retraction/unretraction move.
G20: Set Units to Inches
Example: G20
G21: Set Units to Millimeters
Example: G21
Example: G90
Example: G91
G92: Set Position
Example: G92 X10 E90
Unbuffered M and T commands
M0: Stop
Example: M0
The RepRap machine finishes any moves left in its buffer, then shuts down. All motors and heaters are turned off. It can be started again by pressing the reset button on the master microcontroller. See also M1, M112.
M1: Sleep
Example: M1
Example: M3 S4000
Example: M4 S4000
Example: M5
The spindle is turned off.
Example: M7
Example: M8
Example: M9
M10: Vacuum On (CNC specific)
Example: M10
Example: M11
Example: M17
Example: M18
M20: List SD card
Example: M20
ok Files: {SQUARE.G,SQCOM.G,}
Duet-dc42 firmware returns the (long) filenames in the correct case. If the S2 parameter is present, the file list is returned in JSON format, as a single array called "files". The optional P parameter specifies the directory to list, defaulting to the /gcodes directory.
M21: Initialize SD card
Example: M21
The SD card is initialized. If an SD card is loaded when the machine is switched on, this will happen by default. SD card must be initialized for the other SD functions to work.
M22: Release SD card
Example: M22
M23: Select SD file
Example: M23 filename.gco
Duet-dc42 firmware supports long filenames as well as 8.3 format.
M24: Start/resume SD print
Example: M24
M25: Pause SD print
Example: M25
M26: Set SD position
Example: M26
M27: Report SD print status
Example: M27
Report SD print status.
M28: Begin write to SD card
Example: M28 filename.gco
M29: Stop writing to SD card
Example: M29 filename.gco
Example: M30 filename.gco
filename.gco is deleted.
Example: M31
The response looks like:
 echo:54 min, 38 sec
(Can be used when printing from SD card)
Example: M32 filename.gco
M33
Used by some variants of Marlin firmware. Purpose unknown.
M34
M36: Return file information
Example: M36 filename.gco
Returns information for the specified SD card file in JSON format. Supported by Duet-dc42 firmware. A sample response is:
M40: Eject
See also M240 and M241 below.
M41: Loop
Example: M41
M42: Stop on material exhausted / Switch I/O pin
M42 in ???
Example: M42
If your RepRap can detect when its material runs out, this decides the behaviour when that happens. The X and Y axes are zeroed (but not Z), and then the machine shuts all motors and heaters off. You have to press reset to reactivate the machine. In other words, it parks itself and then executes an M0 command (q.v.).
M42 in Marlin/Sprinter
Example: M42 P7 S255
M42 in Teacup
Not needed. General purpose devices are handled like a heater, see M104.
Example: M43
M80: ATX Power On
Example: M80
Note: some firmwares, like Teacup, handle power on/off automatically, so this is redundant there. Also, see RAMPS wiring for ATX on/off
M81: ATX Power Off
Example: M81
Example: M82
makes the extruder interpret extrusion as absolute positions.
Example: M83
makes the extruder interpret extrusion values as relative positions.
M84: Stop idle hold
Example: M84
On Marlin, M84 can also be used to configure or disable the idle timeout. For example, "M84 S10" will idle the stepper motors after 10 seconds of inactivity. "M84 S0" will disable idle timeout; steppers will remain powered up regardless of activity.
M92: Set axis_steps_per_unit
Example: M92 X<newsteps> Sprinter and Marlin
M98: Call Macro/Subprogram
Example: M98 Pmymacro.g
Runs the macro in the file mymacro.g. In conventional G Codes for CNC machines the P parameter normally refers to a line number in the program itself (P2000 would run the Macro starting at line O2000, say). For RepRap, which almost always has some sort of mass storage device inbuilt, it simply refers to the name of a GCode file that is executed by the G98 call. That GCode file does not need to end with an M99 (return) as the end-of-file automatically causes a return. It is usually a good idea to start a macro with an M120 (Push) instruction and to end it with an M121 (Pop) instruction, q.v. Macro calls cannot usually be nested or be recursive; i.e. you can't call a macro from a macro (though some implementations may allow this).
Example: M99
Returns from an M98 call.
M98: Get axis_hysteresis_mm
Example: M98
Proposed for Marlin
M99: Set axis_hysteresis_mm
Example: M99 X<mm> Y<mm> Z<mm> E<mm>
Proposed for Marlin
M101 in Teacup firmware
If a DC extruder is present, turn that on. Else, undo filament retraction, which means, make the extruder ready for extrusion. Complement to M103.
M101 in other firmwares
Deprecated. Regarding filament retraction, see M227, M228, M229.
Deprecated.
M103 in Teacup firmware
If a DC extruder is present, turn that off. Else, retract the filament in the hope to prevent nozzle drooling. Complement to M101.
M103 in other firmwares
Deprecated. Regarding extruder retraction, see M227, M228, M229.
Example: M104 S190
Set the temperature of the current extruder to 190oC and return control to the host immediately (i.e. before that temperature has been reached by the extruder). Duet-dc42 firmware also supports the optional T parameter (as generated by slic3r) to specify which tool the command applies to. See also M109.
M104 in Teacup Firmware
Example: M104 P1 S100
Set the temperature of the device attached to the second temperature sensor to 100 °C.
Example: M105
ok T:201 B:117
M105 X0
Duet-dc42 extension
Duet-dc42 firmware returns a JSON-formatted response if parameter S2 or S3 is included. This is used by the touch-screen control panel. The response comprises a single JSON object, with no nesting of objects or arrays. It is similar to the object returned by the web interface status request, but some fields are omitted. Here is a sample response when S2 is used:
{"status":"I","heaters":[25.0,29.0,28.3],"active":[-273.1,0.0,0.0],"standby":[-273.1,0.0,0.0],"hstat":[0,2,1],"pos":[-11.00,0.00,0.00],"extr":[0.0,0.0],"sfactor":100.00,
 "efactor":[100.00,100.00],"tool":1,"probe":"535","fanRPM":0,"homed":[0,0,0],"fraction_printed":0.572}
The meaning of these fields is:
status:  I=idle, P=printing from SD card, S=stopped (i.e. needs a reset)
hstat:   status of the heaters, 0=off, 1=standby, 2=active, 3=fault
pos:     the X, Y and Z positions of the print head
efactor: the current extrusion factors (see M221 command)
tool:    the selected tool number. Zero typically means no tool selected.
probe:   the Z-probe reading
fanRPM:  the cooling fan RPM
homed:   the homed status of the X, Y and Z axes. 0=axis has not been homed so position is not reliable, 1=axis has been homed so position is reliable.
The response when S3 is used comprises these field plus some additional ones that do not generally change (e.g. the machine name and axis lengths) and therefore do not need to be fetched as often. In particular, the machine name is returned in variable "myName".
M106: Fan On
yes yes yes yes
Example: M106 S127
Turn on the cooling fan at half speed.
Mandatory parameter 'S' declares the PWM value (0-255). M106 S0 turns the fan off. In some implementations the pwm is specified by a real fraction: M106 S0.7.
M106 in Duet Firmware
Duet-dc42 firmware also supports an optional I parameter. If this parameter is present and greater than zero, the cooling fan output is inverted. This makes the cooling fan output suitable for feeding the PWM input of a 4-wire fan via a diode. If the parameter is present and zero or negative, the output is not inverted. If the parameter is not present, the inverted/non-inverted state remains unchanged. The default at power up is not inverted.
If the 'R' parameter is passed when using Duet-zpl firmware (0.96g+), the last-known fan value will be set. If the 'S' parameter is passed along with 'R', the firmware will not reset the last-known fan value. This may be useful for tool change macro files.
M106 in Teacup Firmware
Example: M106 P2 S255
M107: Fan Off
Deprecated. Use M106 S0 instead.
M108: Set Extruder Speed
Sets speed of extruder motor. (Deprecated in current firmware, see M113)
(See G10) not needed see text yes  ??? yes
M109 in Teacup
M109 in Marlin, Sprinter (ATmega port), Duet
Example: M109 S185
Duet-dc42 firmware also supports the optional T parameter (as generated by slic3r) to specify which tool the command refers to (see below).
M109 in Sprinter (4pi port)
Example: M109 S185 R240 //sets extruder temperature to 185 and waits for the temperature to be between 185 - 240.
M110: Set Current Line Number
 ??? not needed  ???  ???  ??? yes
Example: M110 N123
M111: Set Debug Level
Example: M111 S6
#define DEBUG_ECHO (1<<0)
#define DEBUG_INFO (1<<1)
#define DEBUG_ERRORS (1<<2)
Example: M253
Debug different mechanism
M112: Emergency Stop
Example: M112
M113: Set Extruder PWM
Example: M113
M113 S0.7
M114: Get Current Position
Example: M114
Example: M115
sample data from firmware:
M116: Wait
Example: M116
Duet-dc42 firmware version 0.78c and later supports an optional P parameter, used to specify a tool number. If this parameter is present, then the system only waits for temperatures associated with that tool to arrive at their set values. This is useful during tool changes, to wait for the new tool to heat up without necessarily waiting for the old one to cool down fully.
M117: Get Zero Position
Example: M117
M117 in Marlin, Smoothie and Duet-dc42: Display Message
Example: M117 Hello World
This causes the given message to be shown in the status line on an attached LCD. The above command will display Hello World.
M118: Negotiate Features
Example: M118 P42
M119: Get Endstop Status
yes yes yes yes
Example: M119
M120: Push
  1. Current feedrate, and
M121: Pop
M122: Diagnose
M123: Tachometer value
M124: Immediate motor stop
Immediately stops all motors.
M126: Open Valve
Example: M126 P500
M127: Close Valve
Example: M127 P400
M128: Extruder Pressure PWM
Example: M128 S255
M129: Extruder pressure off
Example: M129 P100
M130: Set PID P value
yes (See M30[01]) See M301
Example: M130 P 0 S 8.0 # Sets heater 0 P factor to 8.0
M131: Set PID I value
Example: M131 P 1 S 0.5 # Sets heater 1 I factor to 0.5
M132: Set PID D value
Example: M132 P 0 S 24 # Sets heater 0 D factor to 24.0
M133: Set PID I limit value
yes
Example: M133 P 1 S 264 # Sets heater 1 I limit value to 264
yes See M504
Example: M134
M135: Set PID sample interval
Example: M135 S300
Debug
Example: M136 P1 # print heater 0 PID parameters to host
M140: Bed Temperature (Fast)
yes yes yes yes Yes
Example: M140 S55
M141: Chamber Temperature (Fast)
Example: M141 S30
M142: Holding Pressure
Example: M142 S1
M143: Maximum hot-end temperature
Example: M143 S275
M144: Stand By Your Bed
Example: M144
Example: M160 S4
M160 S4
G1 X70.6 E0:0:0:42.4
G1 E42.4:0:0:0
obsolete, see M116 yes yes yes
Example: M190 S60
M200: Set filament diameter / Get Endstop Status
yes yes
M200 D0 or M200 D1.128 ; reset E multiplier to 1, since sqrt(1/pi)*2=1.128
Example: M201 X1000 Y1000 Z100 E2000
M203: Set maximum feedrate
Example: M203 X6000 Y6000 Z300 E10000
Sets the maximum feedrates that your machine can do in mm/min.
M205: Advanced settings
M206:
M206 Marlin - Set home offset
Example: M206 X10.0 Y10.0 Z-0.4
M206 Repetier - Set eeprom value
Example: M206 T3 P39 X19.9
Set Jerk to 19.9
Example: M207
NOTE: Marlin defines M207 as "set retract length S[positive mm] F[feedrate mm/min] Z[additional zlift/hop], stays in mm regardless of M200 setting"
M208: Set axis max travel
Example: M208 X250 Y210 Z180
With Duet-dc42 firmware, on a Cartesian printer you can also use this command to specify software limits for axis travel in the negative direction, by adding parameter S1. The axis limits you set are also the positions assumed when an endstop is triggered.
NOTE: Marlin defines M208 as "set recover=unretract length S[positive mm surplus to the M207 S*] F[feedrate mm/sec]"
Example: M209 S1
M210: Set homing feedrates
Example: M210 X1000 Y1500
Example: M211 X1 Y1 Z1 S0
Disables X,Y,Z max endstops
Example: M211 X0 S1
Enables X min endstop
Example: M211
Example: M220 S80
S<factor in percent>- set speed factor override percentage
Example: M221 S70
S<factor in percent>- set extrude factor override percentage
M226: Gcode Initiated Pause
Example: M226
Example: M227 P1600 S1600
P and S are steps.
Example: M228
See also M227.
Example: M229 P1.0 S1.0
Example: M230 S1
Debug: Echo off
Example: M240
Debug: Echo on
Example: M241
M245: Start cooler
Example: M245
M246: Stop cooler
Example: M246
M251 S0 - Reset, S1 - Print, S2 - Store to Z length (also EEPROM if enabled)
(This is a Repetier-Firmware only feature)
M280: Set servo position
(Marlin, Repetier M340)
M280 - set servo position absolute. P: servo index, S: angle or microseconds (Marlin)
M300: Play beep sound
Usage: M300 S<frequency Hz> P<duration ms>
Example: M300 S300 P1000
Play beep sound, use to notify important events like the end of printing. See working example on R2C2 electronics. Also supported by duet-dc42 firmware via the sounder on the add-on touch screen control panel.
M301: Set PID parameters - Hot End
Support Duet Teacup Sprinter Marlin Repetier Smoothie
PIDCHW (See M13[0-3]) PID yes
   Example: M301 P1 I2 D3 ; Marlin
   Example: M301 P1 I2 D3 C5 H1 B20 W127 ; Duet
   Example: M301 P1 I2 D3 T0.2 H1 B20 W127 S0.8 ; Duet-dc42
   Example: M301 S0 P30 I10 D10 ; Smoothie ( S0 is 0 for the hotend, and 1 for the bed, other numbers may apply to your configuration, depending on the order in which you declare temperaturecontrol modules )
Sets Proportional, Integral and Derivative values for hot end. The value C refers to an extrusion rate. The value T is the approximate additional PWM (on a scale of 0 to 255) needed to maintain each additional 1C temperature, used to preset the I-accumulator when switching from heater fully on/off to PID. H is the heater number, default 1 (i.e. first extruder heater). Duet-dc42 firmware interprets a negative P term as indicating that bang-bag control should be used instead of PID (not recommended for the hot end, but OK for H0 which is the bed heater). The S factor is designed to allow a correction to be made for a change in heater power and/or power supply voltage without having to change all the other parameters. For example, an S factor of 0.8 means that the final output of the PID controller should be scaled to 0.8 times the standard value, which would compensate for a heater that is 25% more powerful than the standard one or a supply voltage that is 12.5% higher than standard.
See also PID Tuning.
Alternate implementation
Example: M301 W125
M302: Allow cold extrudes
This tells the printer to allow movement of the extruder motor, when the hotend is not at printing temperature
Example: M302
When using Duet-zpl or Duet-dc42 firmwares, running M302 will only report the current cold extrusion state. To allow or deny cold extrudes/retracts, run either "M302 P1" or "M302 P0".
M303: Run PID tuning
PID PID PID
Hot end usage:
M303 S<temperature> C<cycles>
Bed usage:
Example:
M303 C8 S175
M303 E0 S190
PID See M301
   Example: M304 P1 I2 D3 ; set kP=3, kI=2, kD=3
   Example: M301 P1 I2 D3 T0.7 H0 B20 W127 ; Duet-dc42 firmware
   Example: M304          ; Report parameters
Sets Proportional, Integral and Derivative values for bed. Duet-dc42 firmware interprets a negative P term as indicating that bang-bag control should be used instead of PID. In Duet-dc42 firmware, this command is identical to M301 except that the H parameter (heater number) defaults to zero.
Sets the parameters for temperature measurement. Supported by RepRapFirmware from 0.78c, and Duet-dc42 firmware.
Example: M305 P1 T100000 R1000 B4200
This tells the firmware that for heater 1 (P parameter: 0 = heated bed, 1 = first extruder) the thermistor 25C resistance (T parameter) is 100Kohms, the thermistor series resistance (R parameter) is 1Kohms, the thermistor beta (B parameter) is 4200. All parameters other than P are optional. If only the P parameter is given, the existing values are displayed.
Additionally, Duet-dc42 firmware supports an ADC correction functionality and a thermistor selection facility.
Example: M305 P1 T100000 R1000 B4200 H14 L-11 X2
Here the ADC high end correction (H parameter) is 14, the ADC low end correction (L parameter) is -11, and thermistor input #2 is used to measure the temperature of heater #1.
M306: set home offset calculated from toolhead position
Example: M306 Z0
Implemented in Smoothieware
M320: Activate autolevel(Repetier)
YES
(Repetier only)
M321: Deactivate autolevel(Repetier)
YES
(Repetier only)
M322: Reset autolevel matrix(Repetier)
Example: M322 S1
Parameter S1 is mandatory
YES
(Repetier only)
M340: Control the servos(Repetier)
M340 P<servoId> S<pulseInUS> / ServoID = 0..3 pulseInUs = 500..2500 Servos are controlled by a pulse width normally between 500 and 2500 with 1500ms in center position. 0 turns servo off.
M355: Turn case lights on/off
no no no no 0.92.2 no
Enable lights
M355 S1
Disable lights
M355 S0
Report status
M355
Every call or change over LCD menu sends a state change for connected hosting software like
Case lights on
Case lights off
No case lights
Target
Example
M360
Response
Config:Baudrate:250000
Config:InputBuffer:127
Config:NumExtruder:2
Config:MixingExtruder:0
Config:HeatedBed:0
Config:SDCard:1
Config:Fan:1
Config:LCD:1
Config:SoftwarePowerSwitch:1
Config:XHomeDir:-1
Config:YHomeDir:-1
Config:ZHomeDir:-1
Config:SupportG10G11:1
Config:CaseLights:0
Config:ZProbe:1
Config:Autolevel:0
Config:EEPROM:1
Config:PrintlineCache:24
Config:JerkXY:30.00
Config:JerkZ:0.30
Config:RetractionLength:3.00
Config:RetractionSpeed:40.00
Config:RetractionZLift:0.00
Config:XMin:0.00
Config:YMin:0.00
Config:ZMin:0.00
Config:XMax:250.00
Config:YMax:150.00
Config:ZMax:90.00
Config:XSize:250.00
Config:YSize:150.00
Config:ZSize:90.00
Config:XPrintAccel:250.00
Config:YPrintAccel:250.00
Config:ZPrintAccel:100.00
Config:XTravelAccel:250.00
Config:YTravelAccel:250.00
Config:ZTravelAccel:100.00
Config:PrinterType:Cartesian
Config:MaxBedTemp:120
Config:Extr.1:Jerk:50.00
Config:Extr.1:MaxSpeed:100.00
Config:Extr.1:Diameter:0.00
Config:Extr.1:MaxTemp:220
Config:Extr.2:Jerk:50.00
Config:Extr.2:MaxSpeed:100.00
Config:Extr.2:Diameter:0.00
Config:Extr.2:MaxTemp:220
Example: M400
M420: Set RGB Colors as PWM
Example: M420 R255 E255 B255
M540: Set MAC address
Example: M540 P0xBE:0xEF:0xDE:0xAD:0xFE:0xED
M550: Set Name
Example: M550 PGodzilla
M551: Set Password
Example: M551 Pmy-very-secret-word
M552: Set IP address
Example: M552 P192.168.1.14
Sets the IP address of the RepRap machine to (in this case) 192.168.1.14. A restart may be required before the new IP address is used. If no P field is specified, this echoes the existing IP address configured. If S0 is added thus: M552 S0 P192.168.1.14 networking is disabled.
M553: Set Netmask
Example: M553 P255.255.255.0
Sets the network mask of the RepRap machine to (in this case) 255.255.255.0. A restart may be required before the new network mask is used. If no P field is specified, this echoes the existing network mask configured.
M554: Set Gateway
Example: M554 P192.168.1.1
Sets the Gateway IP address of the RepRap machine to (in this case) 192.168.1.1. A restart may be required before the new gateway IP address is used. If no P field is specified, this echoes the existing Gateway IP address configured.
M555: Set compatibility
Example: M555 P1
For firmware that can do it, sets the firmware to a mode where its input and (especially) output behaves exactly like other established firmware. The value of the P argument is:
P value Firmware
1 RepRap_Firmware
2 Marlin
3 Teacup
4 Sprinter
5 Repetier
M556: Axis compensation
Example: M556 S100 X0.7 Y-0.2 Z0.6
M557: Set Z probe point
Example: M557 P1 X30 Y40.5
M558: Set Z probe type
Example: M558 P0
A Z probe may be a switch (the default) an IR proximity sensor, or some other device. This selects which to use. P0 gives a switch. P1 gives an unmodulated IR probe, or any other probe type that emulates an unmodulated IR probe (probe output is an analog signal that rises with decreasing nozzle height above the bed). If there is a control signal to the probe, it is driven high when the probe type is P1. P2 specifies a modulated IR probe, where the modulation is commanded directly by the main board firmware using the control signal to the probe. P3 selects an alternative Z probe by driving the control signal to the probe low. See also G31 and G32.
Example: M559
M560: Upload web page file
Example: M560
<!-- **EoF** -->
M561: Set Identity Transform
Example: M561
M562: Reset temperature fault
Example: M562 P2
M563: Define a tool
Example: M563 P3 D0:5:6 H1:3
Tools are usually (though not necessarily) extruders. The P field specifies the tool number. Tool numbers can have any positive integer value and 0. The D field specifies the drive(s) used by the tool - in this case drives 0, 5 and 6. Drive 0 is the first drive in the machine after the movement drives (usually X, Y and Z). If there is no D field the tool has no drives. The H field specifies the tool's heaters - in this case heaters 1 and 3. Heater 0 is usually the hot bed (if any) so the first extruder heater is usually 1. If there is no H field the tool has no heaters.
Tools are driven using multiple values in the E field of G1 commands, each controlling the corresponding drive in the D field above, as follows:
G1 X90.6 Y13.8 E2.24:2.24:15.89
G1 X70.6 E0:0:42.4
The first line moves straight to the point (90.6, 13.8) extruding a total of 2.24mm of filament from both drives 0 and 5 and 15.98mm of filament from drive 6.
The second line moves back 20mm in X extruding 42.4mm of filament from drive 6.
Duet-dc42 firmware supports an additional form of the M563 command. The command:
M563 S1
M564: Limit axes
Example: M564 S0
Allow moves outside the print volume, or not. If the S parameter is 0, then you can send G codes to drive the RepRap outside its normal working volume, and it will attempt to do so. User beware... If you set the S parameter to 1 then the RepRap will not think outside the box. The default behaviour is S = 1.
M565: Set Z probe offset
Example: M565 X3 Y4.5 Z-2.37
Set the offset from the extruder tip to the probe position. The X, Y and Z values are the delta between the extruder and the actual trigger position of the probe. If the probe trigger point is below the extruder (typical) the Z offset will be negative. This just records the point offset; it does not actually do the probing. See G32.
M566: Set minimum speeds
Example: M566 X20 Y20 Z2 E10
Work around an algorithm limitation of some firmwares, which can't calculate step timings for a standing start. Teacup Firmware and Smoothieware don't have this limitation, so M566 is obsolete there.
M566 sets the speeds in mm/minute that axes can do from a standing start. If an accelerating algorithm starts a move with a zero velocity on other firmwares and then accelerates from that, it can give problems when the zero initial velocity is used to calculate a timestep between stepper pulses at the beginning: the timestep ends up being infinite... So these systems have initial small velocities to start at. This sets them.
M567: Set tool mix ratios
Example: M567 P2 E0.1:0.2:0.1:0.6
The example sets the mix ratio for tool 2 (the P value). When mixing is then turned on (see M568), only single E values need to be sent on a G1 command (any extra E values will be ignored, but are not illegal):
G1 X20 E1.3
See also M568.
Example: M568 P2 S0
G1 X20 E0.2:0.4:0.166:0.3
The off state is the default.
M569: Set axis direction values
Example: M569 P0 S1
Set the control value for the drive specified by P that sends it forwards to the given value in the S field. After sending the example, sending a 1 to X (drive 0) will make it go forwards, sending a 0 will make it go backwards. Obviously to be used with extreme caution...
M570: Set heater timeout
Example: M570 S120
After a heater has been switched on, wait 120 seconds for it to get close to the set temperature. If it takes longer than this, flag a heater fault.
M571: Set output on extrude
Example: M571 S0.5
This turns an output on whenever extrusion is being done, and turns it off when the extrusion is finished. The output could control a fan or a stirrer or anything else that needs to work just when extrusion is happening. The S parameter sets the value of the PWM to the output. 0.0 is off; 1.0 is fully on.
M572: Set or report extruder elasticity compensation
Example: M572 P3 S0.06
This sets the compensation time in seconds (S parameter) for Bowden extruder elasticity for the specified drive (P parameter). Supported by Duet-dc42 firmware. It has an effect similar to the EXTRUDER_ADVANCE_K factor in Marlin firmware. Normally, compensation should be applied to extruder drives only (drives 3 and higher).
M573: Report heater PWM
Example: M573 P1
This gives a running average (usually taken over about five seconds) of the PWM to the heater specified by the P field. If you know the voltage of the supply and the resistance of the heater this allows you to work out the power going to the heater.
Example: M574 X1 Y2 Z0 S1
This defines the type of endstop switch or opto sensor that the printer has for each axis: 0 = none, 1 = low end, 2 = high end. The optional S parameter defines whether the endstop input is active high (S1, the default) or low (S0). Intended for use with boards that provide a single endstop input for each axis that may be used for either a high or a low end endstop, such as the Duet. Supported by Duet-dc42 firmware. On delta printers, the XYZ parameters refer to the towers and the endstops should normally all be high end.
M665: Set delta configuration (Marlin and Duet-dc42)
Example: M660 L250 R160 S200 (Marlin), M660 L250 R160 B80 H200 (Duet-dc42)
Set the delta calibration variables. L = diagonal rod length, R = delta radius, S = segments per second, B = print bed radius, H = nozzle height above bed when homed after allowing for the endstop corrections.
M666: Set delta endstop adjustment (Marlin and Duet-dc42)
Example M666 X-0.1 Y+0.2 Z0
M906: Set motor currents
Example: M906 X300 Y500 Z200 E350
M909: Set microstepping
Example: M909 X3 Y5 Z2 E3
Set the microstepping value for each of the steppers. In Redeem this is implemented as 2^value, so
M909 X2 sets microstepping on X-axis to 2^2 = 4,
M909 Y3 sets microstepping on Y-axis to 2^3 = 8 etc.
M998: Request resend of line
Example: M998 P34
Request a resend of line 34. In some implementations the input-handling code overwrites the incoming G Code with this when it detects, for example, a checksum error. Then it leaves it up to the GCode interpreter actually to request the resend.
Example: M999
G: List all G-codes
Example: G
This lists all implemeted G-codes in the firmware with description and sends it back to the host.
M: List all M-codes
Example: M
This lists all implemeted M-codes in the firmware with description and sends it back to the host.
T: Select Tool
Example: T1
The sequence followed is:
  4. Use the new tool.
Selecting a non-existent tool (100, say) just does Step 1. above. That is to say it leaves all tools in their standby state. You can, of course, use the G10 command beforehand to set that standby temperature to anything you like.
Some implementations (e.g. RepRapFirmware) allow you to specify tool-change G Code macros. There are normally three specified (any of which can contain no commands if desired) that execute in this order:
  2. (Old tool is released);
With such implementations there is no wait for temperature stabilisation. That can be achieved by an M116 in any of the macros, of course.
After a reset tools will not start heating until they are selected. You can either put them all at their standby temperature by selecting them in turn, or leave them off so they only come on if/when you first use them. The M0, M1 and M112 commands turn them all off. You can, of course, turn them all off with the M1 command, then turn some back on again. Don't forget also to turn on the heated bed (if any) if you use that trick.
Proposed SCARA calibration codes (Morgan)
In order to ease calibration of Reprap Morgan, the following M-codes are used to set the machine up Implemented in qharley/Marlin armlevel branch.
Smoothieware: M364 P0 will accept the current position as 90deg between arms. The offset is stored as a trim offset (M666) and no further user interaction is required except to save all changes via M500
M365: SCARA scaling factor
Clear the map and prepare for calibration Usage:
      M370
      M370 X<divisions> Y<divisions>
M374: Save calibration grid
Saves the calibration grid. (Smoothieware) Usage:
      M374
      M374 <file extension> Z
Without parameters safes the grid into the default grid file that gets loaded at boot Parameter specifies the extension of the grid file - useful for special grid files such as for a special print surface like a removable print plate. Addition of Z will additionally save the M206 Z homing offset into the grid file
Display the bed level calibration matrix (Marlin) Load Grid matrix file (Smoothieware) Usage:
      M375
      M375 <file extension>
Marlin uses these codes to manipulate EEPROM values.
M500: store parameters in EEPROM
Save current parameters to EEPROM. zpl fork of the Duet firmware implements this and allows "S1" to be passed, so changed parameters can be automatically saved to EEPROM.
M501: read parameters from EEPROM
Set the active parameters to those stored in the EEPROM. This is useful to revert parameters after experimenting with them.
M502: revert to the default "factory settings."
This command resets all tunable parameters to their default values, as set in the firmware. This doesn't reset any parameters stored in the EEPROM, so it must be followed with M501 if you want to do that.
M503: Print settings
xx can be one of:
ok
rs
On the latest version of Pronterface and soon Octoprint a special comment of the form:
// action:command
is allowed to be sent from the firmware, the command can currently be pause, resume or disconnect which will execute those commands on the host. As this is also a comment other hosts will just ignore these commands.
ok
start
Exceptions:
1. Marlin 1.0.0 Gen6 Firmware does not follow the two character rule. 'rs' is actually 'Resend' and '!!' is 'Error'. Example Lines:
  • Error: Line Number is not current line + 1. Last Line: 7
  • Resend: 8
  • Writing to File: print.gco
  • Done saving file.
  • File selected
2. Duet-dc42 firmware responds to some commands with a reply string in JSON format, terminated by a newline. This allows for later firmware revisions to include additional information without upsetting clients (e.g. touch-screen control panels) that do not expect it, and to make responses self-describing so that the client will not be confused if responses are delayed or lost. The commands affected are:
  • M105 S2
  • M105 S3
  • M20 S2
  • M36
Problem to solve
Each line of G-code sent from the host to the controller is answered with an ok before the next line can be sent without locking communications up. This slows down communication and limits the number of commands that can be sent per second to the printer controller, as the USB stack on the host and the serial interface driver on the Arduino add their own latencies (up to 10 milliseconds). This is a problem for controllers using native USB as well, because a current technology printer can never print as fast as commands come in.
Alternatives to G-code